How to reduce generator draw when charging batteries

Hi, can anybody advise if it’s possible to reduce my generator draw through the Vrm when charging the batteries ? At the moment it’s running at its max 7kwh, I’d like to reduce to 5kwh so the generator is not maxing out all the time. Also, I don’t want to reduce any solar input by doing this if possible ?


I’ve been through the menus, but can’t see anything

img-7858.png

vrm advanced
img-7858.png (267.7 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

5 Answers
delf67 avatar image
delf67 answered ·

You need to limit your current input on the ACin for the generator. About 22A would be approx. 5KVA @230V (22 x 230 = 5060).

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image kevgermany ♦♦ commented ·
Or 40A for 120V
0 Likes 0 ·
kevgermany avatar image
kevgermany answered ·

Assuming override by remote is on.

On the VRM dashboard, top right is a switch icon. Click on that, gives you the option to set input AC current.

These won't directly affect solar input, but if it does, use @JohnC 's method of slightly reducing the multiplus absorption voltage.


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Jason avatar image
Jason answered ·

I can’t see a switch, does this mean I’ve not got the option ?img-7859.png


img-7859.png (299.7 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mjs500 avatar image mjs500 commented ·
on your device list go in your Quattro 10kva go in to input current limit and set it
1 Like 1 ·
Jasbir Rathor avatar image
Jasbir Rathor answered ·

Hello Jason, This is how I control the INPUT from the generator . On the touch 50 swipe to the next screen, keep on swiping till you see at the bottom part the screen AC Current Limit beside this is AC Mode ON. I think you should have 60 amps at the bottom of the AC current limit. I think it is the default input. Click on the amps from there you should have a small control block with + / - . So from here change the input. There is another way to do it. I find this is the best way to make changes. Good luck.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Jason avatar image
Jason answered ·

Found the switch, doesn’t work in an iPhone but does on an iPad, thanks guys

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image kevgermany ♦♦ commented ·
An update, your pic showed the remote desktop, not the dashboard. From the remote desktop you can access it under settings.
0 Likes 0 ·
mjs500 avatar image mjs500 kevgermany ♦♦ commented ·

but you can from remote console

img-2024-03-10-13-26-15-043.jpg


1 Like 1 ·
Show more comments