Apologies if this has been asked and answered. I have looked around the forum but could not fund this exact issue.
Multiplus 12/3000/120
SmartShunt
CerboGX
Batteries are Epoch 12v 300ah. Batteries have internal BS so not connected to CanBus
The Multi / SmartShunt / an MPPT / and an Orion are all connected to the Cerbo.
The problem is that when I program the Multi in VEConfig using the battery manufacturer bulk charge and float charge settings, (14.6/13.8) I consistently get a variance of .3v between what the SmartShunt reads (and the batteries) and what the multi thinks the batteries are at.
For example, with the Multi set at 14.6 for charge, the batteries want to bulk at 14.9. With Float set to 13.8, the batteries will Float at 14.1. To get the proper parameters for the battery manufacturers recommended settings, I need to set charge to 14.3 and Float to 13.5.
I can't figure out this incongruity. Any assistance/direction that can be provided is greatly appreciated.