Why does my multiplus keep trying to charge while its at or above float?

So, I have a used multiplus 12V 3000VA 120A inverter charger. I just got my lithium batteries in and I have configured the multiplus according to the battery specifications. I usually turn off the multiplus if nothing is going on or if I'm working on it. But when I turn it back on it immediately tries to bulk charge and then goes into absorption mode for the specified two hour time period even though the battery voltage is above the float voltage. Is there anywhere in the settings to stop this from happening? I just don't want the batteries to become abused by the charger unnecessarily.

LiFePo4 battery


1000016268.jpg


Thanks in advance!

battery charging
1000016268.jpg (412.1 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Al avatar image Al commented ·

"I just don't want the batteries to become abused by the charger unnecessarily."

Are your charge settings recommended by the manufacturer?

2 hour absorption without a tail current will overcharge most LFP (unless for periodic balancing)

A float voltage of 13.8V (3.45V per cell) is what most use for the absorption voltage, LFP float at around 3.375V (13.5V) again you will overcharge LFP if it's left charging at 3.45V per cell.

I think your charger settings will abuse your batteries, not the charger, I'd certainly change them!

0 Likes 0 ·
2 Answers
Justin Cook avatar image
Justin Cook answered ·

When you turn it off and back on, you've reset its charge logic so it has to go through its cycle again. Nothing to be concerned about, it can't push current that the batteries won't accept and as long as you've set the voltages per the battery manufacturer's recommendations then you're fine!

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

motorboatin avatar image
motorboatin answered ·

Hm. Figured it'd have a button cell or something for memory... Okay, thanks! I appreciate the quick response!

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Justin Cook avatar image Justin Cook ♦♦ commented ·
If I recall correctly, the "Absorption Time" can be set as low as 1 hour if you'd like; depending on the battery bank, though, that may be inadvisable depending on their charge recommendations - ie Battle Born recommends .5hr absorption per battery or per 100Ah of capacity (though I can tell you're not on Battle Borns) so for example, a 400Ah Battle Born bank would call for 2 hour absorption period... your batteries may have a similar spec somewhere.


Personally I wouldn't worry about it, 2 hours at 14.2v even when unnecessary isn't going to adversely affect any reasonably-built LFP battery bank, but at least you know there's some configurability there if you want it!
0 Likes 0 ·