Where can I find Quattro 8000 24V 200/100/100 AC input wattage consumption for 230V connection. I read the manual but couldn't find it and calculating it doesn't seem right.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
@EdvanZ, The "Technical Specification" sheet should be right around page 23 of the user manual... see attached screenshot for the specs that I believe you're asking for.
Thanks Justin but I'm looking for the power consumption at 230v while max charging the batteries. For the Skylla 100amps 24v 230AC, Quatro 8000 and Centaur 24/16. I can't find that info anywhere.
(28.8v (absorption voltage for 24v) * (max charging current as per spec sheet = 100A for the Quattro 24/8000/100 unit) / 0.94 (efficiency loss)) + zero load power ~= 3 kW
A few rough assumptions in there and rounding - e.g. 94% efficiency was quoted for inverter not charger, but its a good starting point for back of envelope.
What did you get from your calcs/assumptions?
Additional resources still need to be added for this topic
11 People are following this question.