After one and half year running, I get two times this alarm :
Really don't know what's a reason or how to trace a reason of this alarm
Do you have any idea what is reason or how to find a reson ?
Thank you for your help
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
After one and half year running, I get two times this alarm :
Really don't know what's a reason or how to trace a reason of this alarm
Do you have any idea what is reason or how to find a reson ?
Thank you for your help
I got more where that came from.. Wanna see 'em..?
It could be a hardware issue but probably in the settings.. or a combination. Who setup yours..?
Without knowing more about your system, it probably means the battery disconnected for a short period. This is possible in the case of a lithium. It is also possible for a breaker type disconnect to partially and cool down and reconnect.
What other components are in the system, how are they connected.
Sorry. I will try give you more details. Battery is 3x pylontech US3000c
and looks like alarm was in 11:38 today :
0.5V difference, not sure if it's ok
47v is quite close to the cut off voltages for pylontec. Chances are the VRM is missing the lower dip as well.
In short your batteries need a good charge.