phil-garver asked

VM-3P75CT Split Phase - Any issue?

Hello,

As I am building out my new RV system one component at a time, the main issue I have is being able to monitor the shore power current to avoid overloads. I would like to use the 3P75CT to do this at the inbound lines to the panel. Are there any issues with using this in a split phase manner be able to monitor and alert via VRM?

split phaseinput current
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

7 Answers
Mr.Orange avatar image
Mr.Orange answered ·

I have the Victron VM-3P75CT installed in a split phase system. It is working great. It has a little fast update interval compared to the EM530 or EM540 meters. Here is a screen shot of what I see. I love being able to see the reading through Victron Connect. In the settings I have it configured as Phase number to be 3-Phase. ESS has alot fast response time since the energy meter is updating faster compared to the EM24.

1709511325361.png

1709511381776.png


** I did have to put a neutral wire in L3 voltage channel to keep the voltage of L3 at zero. The voltage on L3 would drift up to 60-80 volts.



1709511325361.png (75.2 KiB)
1709511381776.png (24.0 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jdfearl avatar image jdfearl commented ·
So you had 2 neutrals on it? 1 in the neutral and a neutral in L3?
0 Likes 0 ·
ldoes (Victron Energy) avatar image
ldoes (Victron Energy) answered ·

Hi all, split-phase support is in active development. The method given by Mr.Orange can also be used until we release this feature.

6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jrpark22000 avatar image jrpark22000 commented ·
Great, looking forward to the future update!
0 Likes 0 ·
jwy224 avatar image jwy224 commented ·

would this be an update to existing hardware such as the Victron VM-3P75CT where we can just purchase the larger CTs needed for North America power inlet cables or will it be a whole new device?

0 Likes 0 ·
kevinc-63559 avatar image kevinc-63559 jwy224 commented ·

I presume we could just clamp onto the inverter AC-IN wires, which are generally smaller than the panel wires?

Any timeline on formal split phase support? Will it just be a software update or is new hardware more likely?

0 Likes 0 ·
ldoes (Victron Energy) avatar image ldoes (Victron Energy) ♦♦ kevinc-63559 commented ·

Hi @KevinC_63559, we generally don't give estimates for when new products or features are released. All I can say is that we have some units running beta firmware with split-phase support, and I expect this feature to be available for all relatively soon. Can't promise it though.

It's only a software update, no new hardware required.

0 Likes 0 ·
kevinc-63559 avatar image kevinc-63559 ldoes (Victron Energy) ♦♦ commented ·
Thank you! Have one that should arrive today from CurrentConnected. Happy to hear it will just require a software update!
0 Likes 0 ·
kevinc-63559 avatar image kevinc-63559 ldoes (Victron Energy) ♦♦ commented ·
If you need any end-user beta testers please let me know. I have a pair of MP-II 48/3000s working with the VM-3P75CT setup per the Ops instructions along with 500amps of 48V battery. I consider the entire system "test". I'm connected to the USA grid (accident of birth).
0 Likes 0 ·
jrpark22000 avatar image
jrpark22000 answered ·

I too am a US split phase user and want to use this to monitor both legs of 120vac.

Given they are 180 phase and using the VM-3P, I'd assume the monitor would see them as separate phase?

What does the touchscreen show for l1/l2/l3 as well as vrm? Does l3 just show blank, or will it alarm or error as l3 is not used?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jrpark22000 avatar image
jrpark22000 answered ·

I've also asked Victron this question in their recent FB post on Feb 19th. https://www.facebook.com/VictronEnergy.BV?locale=en_GB

No reply yet. I'm fearing the lack of replies to this topic (which I've seen in several places) is not good news. Split phase users in the US market aren't covered with this product.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jrpark22000 avatar image
jrpark22000 answered ·

Thank you both! I've added a VM-3P75CT to my setup and it works just as I'd hoped. I now have visibility to my entire AC load!

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jwy224 avatar image jwy224 commented ·

What CTs did you use? Im also in the US and would love to hook this up to my mains.

0 Likes 0 ·
Show more comments
phil-garver avatar image
phil-garver answered ·

Thank you all for verifying this! One thought / proposed question.... With the way many RV's are being setup in the US right now, the panel comes in with 50amp split phase, they then run a portion of the panel out on a separate 30amp line to the inverter/charger, and then back again to the panel to the segmented circuts. I realize this gives them the ability to do an all-in-one panel, but messes with solutions when we just want to use an Multiplus :).

Proposal / Question... With the 3-phase, could I use 2 of them to measure the inbound 50 amp loads to see overall load, and the 3rd one to monitor just the dedicated circuit to the inverter? I am thinking then I could use it for total load visibility.(until I move the rest of the coach to Victron)

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevinc-63559 avatar image
kevinc-63559 answered ·

Make sure your VM-3P75CT is at current firmware levels (via VRM). Mine was shipped at 1.01 and my Cerbo had a heck of a time with it. Once I upgraded to 1.06 everything stabilized.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.