Does the pass through double when 2 x 10kva quattro inverters are in parallel?

Good afternoon.


Just a quick question.


Does the 100amp pass through double when 2 10kva quattro's are wired in parallel?

Our system is a 3 phase set up combing 2 x 10 kva inverters per phase.


Thanks

quattro 10kva
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
nickdb avatar image
nickdb answered ·

Yip, because you have twice the transfer relays and twice the rating.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

lewis avatar image lewis commented ·

That's Brilliant thankyou

0 Likes 0 ·