question

testor90 avatar image
testor90 asked

Victron ignoring suddenly DVCC *Chargevoltage limit

When charging from the Grid Victron was always controlled via DVCC Charge voltage limit.

The Multiplus stopped always at 55,2 Volts as set in the dvcc.

Now after the Update of the Multiplus II it is suddenly ignoring the settings.

can somebody confirm?

Multiplus-IIDVCC
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
nickdb avatar image
nickdb answered ·

Did you reload your config after the update as it would have been reset to defaults..?

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

testor90 avatar image testor90 commented ·
Yes I wrote settings to the MPII


Can you tell me wich one could affect the MPII ignoring the DVCC Charge voltage?

Sincerely


0 Likes 0 ·
Show more comments
amcarter333 avatar image
amcarter333 answered ·

Nickdb is right. If you read your instruction manual, it warns that you will likely lose some or all of your settings after doing a firmware update. I find this to be true. For example, I did an update recently and only one setting changed and it was critical to the functionality of my 12v 2000 120v Multiplus. It had changed the AC "Frequency" setting from 60 cycle (the U.S. standard) to 50 cycle (the European standard). As a result, I lost the complete inverting capability. As soon as I reviewed all of my settings and corrected it, everything returned to normal.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

testor90 avatar image
testor90 answered ·

Thank you very much,

Can you please tell me what configuration would have changed this?
Or how to change back, so that the MPII is following the DVCC settings?

Thank you!

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

@TestOr90

All of the inverter base programming. When you firmware updated it reset to factory.

So reprogram the inverter.

The GX remains unchanged.

0 Likes 0 ·
testor90 avatar image testor90 Alexandra ♦ commented ·
Thank you, yes i reprogrammed it, but what setting can lead the MPII to ignore the dvcc?




0 Likes 0 ·
thekwchallenge avatar image
thekwchallenge answered ·

Did you resolve this? Im running Seplos V3 BMS with the latest MPII firmware and CVL is being read correclty by the chargers.

I have an issue with grid feed in but thats another issue in another thread. Happy to compare Seplos settings if it helps you.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.