question

villychr avatar image
villychr asked

Multiplus II: trips battery (no load)

I am installing a (new out of the box) Multiplus II 12/3000 on my boat. I have only connected the DC plus and minus (in order to setup the Multiplus before connecting AC). As soon as I connect the DC breaker, the Multiplus trips the battery shortcut protection. The Multiplus on/off switch is off when this happens.

Any ideas?

Thanks,

Villy

PS. It's not reverse polarity.

Multiplus-IIinstallation
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
JohnC avatar image
JohnC answered ·

Hi @villychr

This will be the Multi filling it's capacitors. They're large and take quite a hit.

If you have a spare 12V Pb battery handy, try jumpering it across to precharge them, then switch in your main battery. Usually comes with a spark.

If you're going to do this regularly you could arrange a precharge circuit, Some Li battery makers even have such in their product range, but it's just a resistor really.

6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

villychr avatar image villychr commented ·
Hi @JohnC, thanks. I connected the multiplus to a start battery, it held the voltage OK. Waited about five minutes but the inverter LED didn't come on (which I presume they should), and the Multiplus (Bus-connected) didn't show up in Victron Connect local). How long does it take to fill the capacitors?

With thanks

Villy

0 Likes 0 ·
JohnC avatar image JohnC ♦ villychr commented ·
@villychr

A precharge done that way only takes the spark. Quick.

Does your bms need resetting or something? V on the Multi terminals? I don't know, you'll have to delve..

0 Likes 0 ·
Show more comments