Phoenix Multiplus 12/2500/120 good for LifePo4?

Hi,

I found a Phoenix Multiplus second hand for a decent price. Will I be able to properly charge my LiFePo4 batteries with it? I just realized that it is an older inverter/charger — can I manually set my charging profile?

Thanks!

MultiPlus Quattro Inverter ChargerLithium BatterychargerPhoenix Inverter
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

If the battery type is set to "User Defined" then the absorption and float Voltages are programmable between 12V and 16V in 0.1V steps.
The settings are programmed in with DIP switches and push buttons. In these modern times, it's a bit clumsy but that is the way things were done back in those days.

Study the manual to familiarise yourself with the setup procedures:
https://www.victronenergy.com/Manuals/PhoenixMulti/UKISM010054000-rev00.pdf

6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

shivadas avatar image shivadas commented ·

Thanks again @WKirby
I will then get it (half price of a new one) and figure it out :)

0 Likes 0 ·
wkirby avatar image wkirby ♦♦ shivadas commented ·

@shivadas Do remember as this is an old unit, it does not have VE.Bus. It will not work with a CCGX or anything like that.
Just adding this for information if you have future plans.

0 Likes 0 ·
shivadas avatar image shivadas wkirby ♦♦ commented ·

@WKirby Ok thank you for that info. Does that change my capability to charge the battery via alternator? Do you know how to set that up (I just posted a separate question about charging LiFePo4 with alternator)

0 Likes 0 ·
shivadas avatar image shivadas wkirby ♦♦ commented ·

Hi @WKirby, sorry to dig this back up. Question: I can trigger relays with my 123smartBMS and will use this to turn on charging from my starter battery. I'm wondering though — I know this is a bit of a noob question — Do I need to somehow attach a "stop charging" relay on the Multiplus (12/2500/120), or does it stop charging if set up correctly?

From what I understand I set an absorption at eg. 14.4V and a float voltage at eg. 13.5V — does that mean that it will essentially "switch to 13.5V" at that point, thus stop actively charging, thus overriding the need for a relay?

0 Likes 0 ·
wkirby avatar image wkirby ♦♦ shivadas commented ·

A stop charging relay is a very good idea.
Remember, the BMS monitors each cell of the battery. If one cell goes over Voltage, the pack Voltage may still be withing the charging parameters set up in the MultiPlus. You'd want the MultiPlus to stop charging if a single cell goes over Voltage.