Hello, everybody,

I run a boat with 2 engines and also two batteries for the start.

Both are operated independently of each other.

I have read in other threads that the IP22 with 3 outputs cannot charge 2 batteries with different states of charge individually.

Can the IP43 with 3 outputs meet this requirement?

Greetings Jürgen Lux

charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

5 Answers
mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

Dear Jürgen,

Functionality, with respect to the 3 outputs, the Phoenix Smart IP43 Charger is similar to the Blue Smart IP22 Charger.

Both have in fact an integrated FET battery isolator.

In this way is it possible to charge both batteries with a single charger while keeping the batteries isolated. Charging current is divided among the batteries depending on battery state of charge in combination with battery parameters and other circuit parameters.

Both batteries will follow the same charge cycle. There is no individual charge cycle for each separate battery.

For optimal charging results and battery life use the same cable thickness and length to connect each individual battery.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

THW Fachgruppe Wassergefahren avatar image
THW Fachgruppe Wassergefahren answered ·

Hello mvader ,

Thanks for your answer.

This means that it would be better to buy a separate charger for each battery?

Or is there a charger that charges both batteries individually?

Greetings Jürgen

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mvader (Victron Energy) avatar image mvader (Victron Energy) ♦♦ commented ·

A IP43 charger will be good enough. The batteries are of the same type.

Ofcourse; separate chargers is theoretically better; but will that result in a longer life time of those two starter batteries? I am not so sure.

The point with this is that there is no single truth. And in your case there is no wrong choice either. :-)

0 Likes 0 ·

Stand alone charger is of course OK, but for most applications not needed as a charger with three outputs gets the same results and is far more cost effective

0 Likes 0 ·
tonka avatar image
tonka answered ·

The only useful application for this would be to simultaneously charge two identical batteries who have the same state of charge?


How will the charger know when bulk-charging has to be switched to adsorption? (And after that, top up) By the average voltage?


How does this affect other programs like reconditioning etc. Or is the simul-charging only suited for a quick charge of a couple of batteries?

I’m looking to buy a ip22 30/3, but only if it makes sense to do so.


We definitely need some more explaining from the Victron folks about this. :-)


Much appreciated!


Tonka.

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mvader (Victron Energy) avatar image mvader (Victron Energy) ♦♦ commented ·

Hi, you wrote:

> The only useful application for this would be to simultaneously charge two identical batteries who have the same state of charge?


No. If at different state of charge,the current will first only go to the most empty battery; and once at equal voltages (while being charged) to both.

Worded differently: its one charger, with one algorithm, and you can connect three batteries to it without a load on one battery also drawing from the second.

See also Argo FET Isolator documentation on our website.

I hope that explains it!

0 Likes 0 ·
Show more comments

First of all, we are talking about starter batteries which typically are never discharged (for more then a few %) so the charger is there to make sure the self discharge over time is compensated. But lest suppose these batteries were stand alone house hold batteries and one set was 50% discharged and the other lets say 90%. Then the charger with three outputs tries to raise the voltage to its setpoint (the absorbtion voltage of lets say 14.4Vdc), This will take time as the "emtpy" battery has the lowest voltage and will absorb most charge current/energy. So in this stage the SOC of the lowest is brought up to become more equal to the other. At a certain point the SOC will be more or less equal and the charge current will divide itself over the two banks (or three banks if there would be a third bank as well). Finally the absorbtion voltage is reached which triggers the absorbtion period (wich implicates that the SOC of both sets is more/less equal) and then the absorbtion period tops the banks up to 100%. So in short, For starter batteries the three way output charger is ideal as it takes care that all remain full as they are. When having a starter and household bank or such this works as well but you need to realize that the charge capacity is divided over the various banks which means you have to take care the charger is powerfull enough.

0 Likes 0 ·
Show more comments
THW Fachgruppe Wassergefahren avatar image
THW Fachgruppe Wassergefahren answered ·

Hello,

Yes, they're two identical batteries.

Thank you for your comments.

Now I have actually only the agony of the choice.

I must now

Compare IP22 and IP43 and consider what the better choice is.

What would you recommend.


Boat:

2 motors

2 batteries a approx. 100 Ah

Both batteries/motors are separate from each other.

Greetings Jürgen

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

shaunthomson avatar image
shaunthomson answered ·

Thanks for the answers on this. I have an extension to this question.

I have 2 battery banks:

House battery: 4 x 12v Lithium 400ah and;

Starter battery: 2 x 12v Deep Cycle

I have the Phoenix IP43 3 output.

Can I connect this charger to both battery banks?

Can I use a lithium charging algorithm?

What is the best solution for this setup?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

6ixgun avatar image 6ixgun commented ·

You probably already figured this out but this is NOT a 3-channel charger with independent algorithms - so no you cannot mix battery chemistry. I would think for what this unit costs we certainly would be able to so - but nope ! Another miss as far as I am concerned. We purchase the IP22 chargers for that reason - but they can't connect with Cerbo so there is pros and cons of that too. Sure wish Victron would simply make universal coms across all their products.

0 Likes 0 ·