question

mmx01 avatar image
mmx01 asked

Victron EasySolar II + MultiPlus II in parallel 1 phase operation

Hi,


EasySolar II shows as combination of few budling blocks and the inverter reports as Multiplus II 24/3000. For parallel single phase operation, is it compatible to connect MultiPlus II like this one: PMP242305010 with EasySolar? The latter has got PN: PMP242307010.


Both are 24/3000/70-32 with new revision 010 but then part of PN: 3050 does not match 3070.


Want to avoid "we will not talk to each other" software wise. I am looking for single phase parallel operation for increased VA capacity for periods of peak usage with AC, Kettle, Boiler etc.


Regards,

Mariusz


multiplus in parallel
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
snoobler avatar image
snoobler answered ·

https://www.victronenergy.com/live/ve.bus:manual_parallel_and_three_phase_systems

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image
marekp answered ·

@mmx01

I have ES-II 48/3000 and MP-II 48/3000 and they work well in parallel.

If HW Rev # is the same there should be no problem.

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mmx01 avatar image mmx01 commented ·
Thanks! I ended up getting another ESII and put them in parallel. I will wire 2nd string of solar into it.


Also pricing is interesting MPII 24/3000VA is around 1100 eur, ESII is around 1300 eur but it includes 250/70 for 600 eur and GX is probably another 200 eur. So this unit is IMO really good value for money.


I needed to disconnect 2nd GX and rewire smartsolar ve.direct from the slave into the main unit but works good otherwise.

0 Likes 0 ·
marekp avatar image marekp mmx01 commented ·
@mmx01 You will have to disable on GX unit.
0 Likes 0 ·
Show more comments
awollheim avatar image awollheim commented ·

I am curious, is your ES-II 48/3000 and MP-II 48/3000 still talking to each other?

Mine stopped talking a few days ago and my installer says it has to due to a software update.

I am finding this hard to believe.

The MP-II gives a low battery warning constantly while the ESII shows the batteries as full.

0 Likes 0 ·
marekp avatar image marekp awollheim commented ·
My system has been working without problem for the last 2 years so I did not need to upgrade its FW.
0 Likes 0 ·