Hi All,
I NEED HELP!
I am dealing with this issue since 4 months, please some-one help me, I posted here 2 threads, I emailed Victron, I talked with the Dealer, post on Reddit and nothing.
[@Victron staff]
I have an installation with the following :
9 x Victron 15 kVA Quattro ( 3 inverters / phase)
3 x Fronius 25 kW on the AC output 1
80 x Pylontech US2000C
I get VE Bus Error 5 and VE Bus Error 18, the wiring is correct, no issue on that, the settings are correct Victron on ESS as suggested by Victron and Fronius are setted up with MG50 and control via modbus.
I get the error only when there is high sun and we have production over 25-30 kW from the Fronius inverters, if the weather is not ok then the system is working fine without any issue, this also confirms that there is not problem on the wiring.
PS never had an issue during the night-time.
As I see, the problem is that the Fronius inverter is still producing to much even if the Victrons tell them to stop and that how there is a high voltage on the AC side, I have checked the graphs whenever the victron stops due to these errors, the voltage is around 240 V - 243 V, which should not be an issue. The Frequency is around 51 Hz.
what can I do to eliminate the issue, because now it`s really annoying, our client is calling us daily that the system is not woring, just today the system stopped working for 9 times and had to restart it.
As you will se below, the error comes from 11 o clok till 15:30 exactly when there is the biggest sun.
Please help me with this!