Should the solar arch on my boat be grounded? I'm reading ~60V AC from the metal support

I have the Multi RS Solar on my boat that is connected directly to 5x550W solar panels in series. The Multi is grounded. The inverter AC output is connected to a breaker box. Even when all the breakers are turned off I can measure ~60VAC from the solar arch whenever the inverter is on. I sometimes feel slight electricity when holding the solar arch.

Why is the Mutli RS sending AC power out to the connected solar panels?


solarGroundingMulti RS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Alexandra avatar image
Alexandra answered ·

@nick5000

It is possible induced voltage (capacitive coupling). Check with a low resistance/impedence meter. With alot of normal DMM meters often it reads a 'phantom' voltage. There is a fancy name for it. But I do know the meter type changes whether it is 'there' or not.

If you are able check the frequency of the AC voltage.

Real question is do you feel a tingle when you touch it. Or someone who is sensitive to those kinds of things? I know I pick up voltages where my husband does not.

8 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
On a different note. Make sure the voltage isn't being transmitted from actual AC lines through the boat.
0 Likes 0 ·
Show more comments
nick5000 avatar image nick5000 commented ·

Thanks, yes I feel a tingle sometimes, if the deck is wet especially. Does that mean it's not a phantom voltage?

I used Mastech ms2108a

0 Likes 0 ·
Show more comments
Paul B avatar image
Paul B answered ·

I would suggest that the solar arch be grounded as a priority as this can cause lots of issues if you have a lighting strike or even a side strike, and it will also remove that tingly feeling you get sometimes. I would suspect that one of the panels maybe leaking to earth as you dont have any connections currently to the frame from what you say. anyway any metal structures above deck should be grounded.