I have 5 remote off-grid surveillance sites utilizing these charge controllers. The installation age ranges from ~5 years to 2 weeks. I have never had an issue with the load cutoff behavior until a couple of months ago when the days got shorter and cloudier. I noticed the issue because the remote camera feeds were unexpectedly shutting down. I've traced this back to load cutoff misbehavior. All 5 of these units are cutting off the load from ~0.5 to ~1.0 volt above the configured value. All controllers are configured and monitored via 'VE.Direct to USB' cables through 'SX Virtual Link' to 'Ubiquity' wireless LAN extenders. Some sites also have a PicoLog data logger attached for troubleshooting. I reset all to 'default' and made the following changes: ABS 28.6v, ABS Max Time 3.0 hrs., Float 26.6v, EQ 31v, load low 23.23v, load high 26.26v. Everything else is default, including 'streetlight = off'.
Has anyone else observed this behavior?