question

svitek avatar image
svitek asked

Quattro II doesn't accept generator on AC In1

I have the same problem as some others. Quattro II doesn't accept my Generator Hyundai D7000 EMS.

The generator is on, it produces 223 V on AC 1 IN, the Quattro switches to charging (there is also Float lighting on the Quattro which doesn't make sense to me, because the batteries Victron Smart are empty), and after a dozen seconds, the generator is disconnected with alarm message AC Input Not Available. The voltage on the AC input is stable at 223 V, the generator is normally working and produces current.

I have tried:

1) UPS Function disabled
2) Weak AC Input enabled
3) AC Input current limit 14 A (On the generator is written that it produces 22 A)

I have read the threads:
https://community.victronenergy.com/questions/177568/generator-runs-but-doesnt-connect.html
https://community.victronenergy.com/questions/37642/generator-ac-disconnected.html

And still don't know what to do to make it work. Has anybody any clue?

MultiPlus Quattro Inverter ChargerGenerator
5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
kevgermany avatar image
kevgermany answered ·

Assuming it's a US unit with 220V split phase, check the voltage on each leg compared to neutral. And to earth. You may need to connect neutral and ground to stabilise this. Hopefully someone who knows USA power can confirm.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

JohnC avatar image
JohnC answered ·

@Svitek

That 'AC Input Not Available' alarm suggests the genset output is baulking at the instant load hit, then possibly self-resetting after a time. You could test for this with a light on another genset outlet.

Try switching on Dynamic Current Limiter in the Quattro. It's like a soft-start, and most gensets benefit from it.

The Weak AC setting is best avoided long term as it comes with power factor and charge limit issues. Shouldn't normally be needed.

https://www.victronenergy.com/live/multiplus_faq

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

svitek avatar image
svitek answered ·

Must tell that grounding was the problem! I improved grounding of the gen and AC out and it started to work normaly. So easy.

2 |3000