Is there a discrepancy with the declared power rating for the Multiplus II 5000 as shown below:
In my situation, I was looking to parallel an extra 5000VA MP2 to my existing set-up, but the National Grid has advised the maximum export connection is 8.4kW and I would therefore need G100/2 for export limitation. However, the existing G100 declaration by Victron is insufficient for G100/2.
Hence, is there a discrepancy with the UK ENA G99 declaration for the 5000VA ??
The small details in this case matters - is it 8.8kW or 8.0kW, as the latter only needs G99 and avoids the self declaration G100/2 and costly witness testing route...
KR
Steve B