Single Phase Fronius Primo at 3 Phase ESS

Is it allowed to connect a Fronius Primo 3.6-1 to one ACout1 from one of the 3 MP2?

Or is it just recommended to connect a 3 phase Fronius to a 3 Phase ESS?

Multiplus-IIESSFronius
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

As long as you are within the factor 1.0 rule it's totally fine.

https://www.victronenergy.com/live/ac_coupling:start#the_factor_10_rule

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

groove avatar image
groove answered ·

Thanks for the reply.

I set up only the first MP2 and used the saved config for the other two as well.

If I connect the Fronius to ACout to e.g. L1 the ESS master, do I need to and can I use the updated config to update the slaves?

Or is it not needed?

2 |3000