question

Mikael avatar image
Mikael asked

Problem with Pylontech SOC after SmartSolar upgrade to 1.42

Hi


After remotely from VRM upgrading SmartSolar to 1.42 my battery doesn’t get charged fully. It charges to example at 92% and today 89% and then just stops and only matches the solar yield to the DC consumption even when there is lots of sun.


I got an error “#68 Network misconfigured” from the SmartSolar after upgrade so I had to exclude it from the SmartNetwork. That is clearly show on the graphs as the big dip starting 2019-04-24.

Both times it has got back to SOC 99 or 100% was after a shutdown and power off whole system and starting it up again.


I have notice the BMV-712 in not correct in SQC and stated 100% when the battery is not. But the VenusGX is set to use Battery Monitor “Pylontech battery on CAN-bus”. Can it be the BMV that is still being in control of SOC in some way? SmartSolar is disconnected from the SmartNetwork but it still feels like it stops charging when BMV get near 100%


The system has been working very good until now.

I have checked the settings against https://www.victronenergy.com/live/battery_compatibility:pylontech_phantom


Pure DC system with 3500w PV and

VenusGX (2.33)

SmartSolar Charger MPPT 250/100 rev2 (1.42)

BMV-712 Smart (4.01)

Pylontech US2000B.


512 = Pylontech
260 = BMV-712 Smart



This is a remote location and I can only use VRM unless I take the trip there.

MPPT ControllersBMV Battery MonitorPylontechVenus GX - VGX
1564648640704.png (82.0 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Mikael avatar image
Mikael answered ·

The problem is now solved, it was a bad connection at one of the cables in the end.


1566964558843.png (139.6 KiB)
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Thanks for the update @Mikael

To help us and others, what cable had a bad connection?

0 Likes 0 ·
Mikael avatar image Mikael Daniël Boekel (Victron Energy Staff) ♦♦ commented ·

The crimping on the positive cable at the SmartSolar had come lose or at least somewhat lose.

0 Likes 0 ·
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Hi @Mikael


An explanation of error #68 is here - https://www.victronenergy.com/live/mppt-error-codes#err_68_-_network_misconfigured


It is always the case that multiple SOC meters will not agree.


With the SmartSolar disconnected from the Smart Network, the pylontech battery is controlling the charge. This is interpreted by the DVCC system inside the GX device too, as explained here - https://www.victronenergy.com/live/battery_compatibility:pylontech_phantom#my_system_only_charges_the_battery_to_52v


There has been a change in charging voltages to improve reliability of the system, with virtually no decrease in actual usable capacity.


While the system is behaving differently from how you have become used to, from your photos, it still appears to be working well.


I am not sure why you have a BMV, when the Pylontech provides it's own State Of Charge reading. There is no harm done with your current configuration, but it is deliberately absent from in the Pylontech and Victron manual. Having multiple States Of Charge only adds to the confusion, and in this case the integrated Pylontech is the more accurate one you should be using.

6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Mikael avatar image Mikael commented ·

Thanks @Guy Stewart (Victron Community Manager)

I will disconnect the BMV tomorrow from the VenusGX and see it that helps. Just leaves it connect to the shunt but not to the Smartnetwork or VE.Direct as a stand alone device would not interfere with the rest of the system, correct?

I will try to adjust the BMV to show more correct SOC as it's a nice and quick way to see battery status without having a phone or computer at hand.

0 Likes 0 ·

Hi @Mikael,

Sorry if I wasn't clear, now that you have the BMV installed, it is not necessary to remove it. Now that the smart network is disabled, it will not make any difference to the behaviour you are seeing.

It is understandable to want to have a clear state of charge display, though in my opinion this is best done with the colour control gx ;)

Now, with the equipment you have, I would suggest playing with the parameters of the BMV to more closely match the reading of the Pylontech. It would seem from your image that it is resetting to 100% too soon, so perhaps extending the time required, or raising the voltage point threshold in the BMV.

No rush on that though, and no need to make a special trip out to your remote site.

0 Likes 0 ·