Orion 24/12-70 Shut down Battery System Pylontech 24 volt Up 2500


Hello Guys, I have a problem with an Orion 24/12 70 and a battery system 2x 24v up3000... when I activate the Orion the batteries give me an error .. Without the Orion everything else work fine multiplus Mppt lights etc ... does anyone know why this could happen?

PylontechOrion DC-DC Converters not smart
img-9434.mp4 (33.1 MiB)
6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Mike Dorsett avatar image Mike Dorsett commented ·
what battery error does the BMS report?
0 Likes 0 ·
Show more comments
jjduke avatar image jjduke commented ·
Besides the BMS error code, do you have any load on the 12v side when you “activate” the Orion? Have you tested for a short in the 12v wiring?

A small load shouldn’t be a problem.

0 Likes 0 ·
Show more comments
kevgermany avatar image kevgermany ♦♦ commented ·
Are you using the Orion to charge the Pylontechs? From a 12V supply?

If so you have the wrong one. The 24/12 means 24V in, 12V out.


0 Likes 0 ·
Show more comments
1 Answer
luisrodriguez avatar image
luisrodriguez answered ·

some one say to me that meaby its a pre charging problem … i was thinking on turn off the battery and starting the system with ac conected to the inverter and see what happens … worse case escenario o lose a fuse ?