Hi developers,
@Guy Stewart (Victron Community Manager) , @mvader (Victron Energy)
It's me again, with another issue that I found on my Multi RS Solar system.
The configuration is like the one attached below and it happens as follows:
1. Battery reaching 14% and after 30 second the grid is connected and the battery is starting to charge.
2. Battery reaching 15% during charging and the grid is disconnected and the battery is starting to discharge.
3. Go to (1) and repeat indefinitely. See below the picture from VRM.
Now....
If I change the end condition "Disconnect AC input on" on anything else than "Absorption finished", for example "Bulk finished" or "Battery voltage", this is going normally... Also seen on the picture from VRM.
Is it possible that the "last state" being somewhere stored like "absorption finished", because the previous cycle was complete until the float state, to be read by the function that decides when to disconnect the grid and therefore decide to disconnect?
Maybe a "reset state" somewhere when "connect to grid" is performed?
Thank you!