Use of Virtual Switch im Multiplus II Parallel System

I have set the virtual switch in my system with two Multiplus II 48V 5KVA to use the AC in only when batteries are lower tha a certain value.

Settings are as follow:

Accept AC in when batteries are lower than 51.90 volt for 60 seconds;

Do not accept AC in if batteries are higher than 52.20 volt for 120 seconds;

I have also set in VS option do not switch off within 5 minutes from switch on.

Despite my settings I am noticing that the system acts in its own way and continue to go in passthrough every two minutes.

virtual switch
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

snoobler avatar image snoobler commented ·

Post your VEconfig VS ON and VS OFF screens.

0 Likes 0 ·
giampaolo avatar image giampaolo snoobler commented ·

Here are the screens of my VS in VE config file.

vs1.jpg

vs2.jpg

vs3.jpg

vs4.jpg

0 Likes 0 ·
vs1.jpg (78.7 KiB)
vs2.jpg (90.1 KiB)
vs3.jpg (92.6 KiB)
vs4.jpg (84.9 KiB)
1 Answer
giampaolo avatar image
giampaolo answered ·

It seemed to me that I posted a reply but there is no trace.

Here are the screens of my settings.

vs1.jpg

vs2.jpg

vs3.jpg

vs4.jpg

Hope this can help.


vs1.jpg (78.7 KiB)
vs2.jpg (90.1 KiB)
vs3.jpg (92.6 KiB)
vs4.jpg (84.9 KiB)