question

tareq avatar image
tareq asked

BMV-712, Battery Monitor

Hi Everyone,


I have a site with 2 battery banks, and I have 2 units of BMV-712 (one per each).


However, the BMVs have been calibrated when the batteries were full, but I found out later that the BMV readings are different from the real SOC

E.g. the SOC was 80% on BMV, however, on it was 20% on the batteries themselves.

What should have made this critical difference? Why the BMV is not giving the correct state of charge?

The batteries are Li-ion and each bank has 15 units of 100Ah).

Kindly advise.

BMV Battery Monitor
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matthias Lange - DE avatar image Matthias Lange - DE ♦ commented ·
Please give us some more details.

What batteries do you have exactly? How is everything wired? What are the settings of the BMV?

0 Likes 0 ·
tareq avatar image tareq Matthias Lange - DE ♦ commented ·

Dear Mathias,

The images below show how are the batteries connected to client cabin and the BMV settings.


The batteries are Huawei.

We have 30 batteries in total.

screenshot-20240106-170627-samsung-notes.jpg

screenshot-20240106-170837.jpg

0 Likes 0 ·
Matthias Lange - DE avatar image Matthias Lange - DE ♦ tareq commented ·

To be honest I don't understand that drawing. Where are the loads connected?

All batteries need to be connected to the battery side of the shunt.
In you drawing there are 10 batteries on one side and 5 on the other side of the shunt.

At last the Peukert exponent is wrong, for lithium it should be 1.05.
The charged volteage seems a bit high.

0 Likes 0 ·