Hello, we’re trying to set up a new charging system on our sailboat. (12volt)
We have 2 365watt panels. We think we’re supposed to wire in series then to our 15amp breaker. Then to our Victron mppt150-60TR controller.
From the mppt to a 60amp maxifuse and then to the house batteries bank (3 4D AGMs)
Any advice? Thanks
We measure 6’ between the mppt & the batteries. We have 4awg(25mm) wire. Do you think that size would be sufficient?
https://www.calculator.net/voltage-drop-calculator.html I work that out to a voltage drop of 0.18 volt (say 0.25v if you inclide a fuse+holder).
Thanks for the link on wire size/voltage drop.
Now about the fuse. Our salesman supplied this MAXI FUSE. (Along with the 4awg wire) Did he chose wrong?
Would this fuse type be acceptable?
4 awg will be ok, fuse holder looks v/good.
I would use a 70a (maybe even an 80a) fuse.