Two Victron Multiplus connected at same house MPII5000 48V + MPII1600 48V

HI!

I have two multiplus systems. One at home(MPII5000), another one at a cabin MP1600 (easily transportable).

During lots of time I don't use the cabin setup.

1 - Can I use both at home?

Something like this:

1704157005092.png

Thanks in advance,


Multiplus-II
1704157005092.png (16.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Rob Duthie avatar image
Rob Duthie answered ·

Hi

Not realy, they need to be the same size and model, drawing not correct with loads and grid?

and AC in where is AC out?

Regards

Rob D

NZ

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rampage avatar image
rampage answered ·

Electrical it isn't an problem, as long as you only connect like the picture. But the second Multiplus will remain dumb. And whit no mmpt or anything else connected there is not really an pro when doing this...