Hi all
I am having some strange Low voltage alarms thrown by the Multiplus when drawing high amps.
The system is installed in a boat with:
- 12v/3000/16Amp Multiplus
- 2 x MPPT
- 1 x Orion DC-DC
- Cerbo GX
- SmartShunt
- TaoBMS
- 8 x 310amp PRISM cells set as 2P4S for a 12v battery
The system was setup about a year ago, it has never been a problem cooking with the induction hob and drawing over 150Amps.
When the batteries are resting, these rest at around 13.3v, and when drawing over 100amps, these deeps below 13V, sometimes around 12.8V. And this is causing the Multiplus to throw a "Low Battery alarm" and restart.
As you can see in the screenshot below, there is a reset event every time the draw goes to around 100amp.
I have been checking the configuration of the system and I cannot see why this would be happening. Note that I have not setup any ESS assistants.
I have also checked the alarms setup in the SmartShunt and these are set to when the voltage drops to 12.4, and as you can see in the VE.Bus screenshot, the voltage never goes that low. (I was observing in realtime, and never went below 12.83v)
What am I missing?
What should I be looking at?
Thanks in advance for your help
Regards
Andres