jayjay asked

Low voltage on the master inverter only

Hello,

We installed three Quattro 10kW for a three phase system with lithium battery storage. The master inverter's low battery light is on, while on the other two inverters the light is off. Also, on the color control as well as on the battery's display, the battery voltage is 50V (70% SOC).


Can anyone advise the reason for this warning?

Lithium Batteryquattro 10kvalow battery warning
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
marekp avatar image
marekp answered ·

@jayjay

Did you check the fuse?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

tnt369 avatar image
tnt369 answered ·

In a three phase system only the master shows the status by LED. The other two units are slaves and don't show their status. Check the DC voltage and connection to all three units.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image
marekp answered ·

@tnt369

In the 3 phase system there is no one master. All three units are masters for respective phases.

Master and slave exists in the parallel connections.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.