Inverter/Chargers combine question

Hello,

If I combine two Inverter/Chargers, lets say Victron Multiplus - one on 220v 1600W and the other on 110v 1600w can I rely on 3200W power supply?

multiple inverters
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
klim8skeptic avatar image
klim8skeptic answered ·

@Samaya You can not combine the output from a 120vand 230v inverter.

Very bad things will happen should you try this.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Kevin Windrem avatar image
Kevin Windrem answered ·

Even if you match the output voltages with a transformer

Very bad things will still happen.

Victron inverters can be paralleled only with specific programming and interconnected VE.Bus as well as specific interconnection cabling (both AC and DC). There's a manual for this.

But mixing a Victron with another inverter or even two Victrons that are not set up for parallel operation will be very bad.