DC wiring to MPPT PV side

Good day, I am currently checking if the wiring between my db board DC breakers from the PV side and MPPTs are correct after i recently had an MC4 connector melted on the PV side. The installer originally installed 4 wires per mppt (pv side), so that is 2 for positive side, and two for negative side wired to the MPPT, coming from 2 DC breakers on the DB board (multiple arrays). Some of the wires are 4mm2 and some are 6mm2. I have a 250/100 and two 150/100's. There are parallel arrays of 300w panels coming in.

My questions are:

1. Is it fine to have 2 wires connected to MPPT PV positive terminal, and two wires connected to the MPPT PV negative terminal, or should i rather connect the 2 DC breaker outputs together and run a single pair from the DC breaker to the PV side of the MPPT?

2. The MPPT spec states max thickness of the incoming wire of 2AWG. For the PV side, is there a minimum thickness the wire must be?


MPPT Controllerswiring
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
kevgermany avatar image
kevgermany answered ·

MC4 limit is 30A. Use a pre made Y cable to join as needed. Size input cables according to current (and voltage drop if the cables are long).

Make sure connectors are crimped properly with the correct crimping pliers.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Jason - UK avatar image
Jason - UK answered ·

@dirkme911 This doesn't sound like a standard PV array set up. Do you have a schematic of your system wiring arrangement? Also what is the Voc & Isc of the panels? Im thinking you need to go back to your installer and get them to verify the installation, or get an opinion of another installer.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

dirkme911 avatar image
dirkme911 answered ·

20231221-185312.jpg20230427-191112.jpgThe installer disappeared after installation, according to the previous owner of the house. And at the moment I want to do as much as I can before calling someone. The system has been working for some years, I just want to know whether the cabling is correct with 4 wires per MPPT on the PV side.

What I have learned so far, is that there are 3 MPPTs, connecting to various strings of 300W panels.

There are 7 strings in total connecting to the 3 MPPTS. The voltage is normally around 120V on the PV side of each MPPT. Amps peaks at around 35A per MPPT. Another reason I am asking, is I am deciding on replacing existing PVC trunking with larger one 100mmx40mm(to cater for the existing 12 wires and possible future expansion), or use the existing 40mmx40mm PVC trunking size, and only have 6 wires going to the MPPTs, in which case the existing trunking can stay.