Alright, after 4 hours I give up. I have miserably failed to set even one working alarm in the VRM.
What I have:
1) Multiplus 24v 5000
2) Cerbo GX
Both are running latest firmwares. Both are supposed to be installed in a boat but for the time being I have them on my bench for testing purposes.
I wish to cover various bad scenarios with alarms:
1) Multiplus dies completely, thus charging/inverting stops. I wish to have an alarm which will trigger an iOS notification AND an email.
2) Multiplus looses shore power. Alarm similarly must trigger.
3) some more scenarios but for the time being I havent even able to make scenario (1) work!
So, trying scenario (1) has led me after hundreds of hit and miss tries to do this:
a) create new alarm for "VE.Bus System [276]"
b) set to ON (triggers) the "Off" "Fault" and "Power supply" and save the alarm
Then I disconnect the Multiplus from the AC IN (so it dies) and wait and wait..... 10,20,30 minutes later nothing.... If i reconnect the AC IN then after a couple of seconds I receive 2 emails and 2 notifications in the iPhone:
1) VE.Bus state: Fault, wait time: 60 seconds
2) VE Bus state: Absorption, wait time: 60 seconds
So instead of receiving the 1st email & notification 1 minute AFTER the disconnection of the Multiplus, I receive them right after I connect the power back to it AND I receive the 2nd email & notification 1 minute later!!!!
What the hell is going wrong??? Please help!