Im questing this because in the manuals say that Quattro 10 kVA ca be connect up to 6 groups of 3 units however in the web page says 4 of 3
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Im questing this because in the manuals say that Quattro 10 kVA ca be connect up to 6 groups of 3 units however in the web page says 4 of 3
5 units per phase maximum in a three phase system.
So 150kVa max system size using the 10kVa in three phase parallel.
See maximum sizing in the three phase manual.
The 6 max is for single phase application.
4 X 3 (12 units) is the max for the 15kVa.
It's a 120V unit so I guess the manual is referring to a split-phase system not 3-phase.
I think it's a typo in the manual.
The 10kVa datasheet says 4 sets of 3 can be parrallel connected for a max of 120kva.
The split phase complicates? it a bit definitely.
Would make sense to find a local dealership since the totals per phase and the totals for 3 phase differ alot when in split phase as well. 120kVa is a pretty big complicated system
The three phase manual could be refering more to the 230v versions. Since you have to have pairs in a split phase so 5 per phase would be impossible. Unless you are not running split phase