Im questing this because in the manuals say that Quattro 10 kVA ca be connect up to 6 groups of 3 units however in the web page says 4 of 3
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Im questing this because in the manuals say that Quattro 10 kVA ca be connect up to 6 groups of 3 units however in the web page says 4 of 3
5 units per phase maximum in a three phase system.
So 150kVa max system size using the 10kVa in three phase parallel.
See maximum sizing in the three phase manual.
The 6 max is for single phase application.
4 X 3 (12 units) is the max for the 15kVa.
It's a 120V unit so I guess the manual is referring to a split-phase system not 3-phase.
I think it's a typo in the manual.