Hi I’ve got a loan unit which is a Quartto rather than my multi 2 5k, the issue that I have with my one is it would balance the grid and got a phantom draw of 500watts every now and again and would also never 0 my smart meter HUD even on -30 grid set point anyway that’s off to Victron to fix.
The issue that I have is the Quattro will not supply my loads on AC in like the Multi 2 even though it’s can see the overall load say 1000watts it would rather split it 50/50 with the battery and the grid. Ie my washing machine and tumble dryer are on mains in with the CT monitoring the load from them on AC 1 in.
Im waiting for the shop to get back to me on this as they are swamped at the mo and I have an ever growing number of cloths to be washed and would rather the batteries take this load fully.
Ive tried shutting power from the grid but no power flows back when thinking about it now this could be down the the ET112 that I’m having to use ie grid goes down ET112 is out for the count on the grid side, as it’s a Quattro I can’t use my CT. The Quattro does when set to -3000 supply back to the grid so bidirection kind of works it’s strange.
Does anyone know what could cause this to happen is there a setting in the Quattro that is different to the multi? System is ESS with the PV assistant.
Thanks in advance