Multiplus II: What is the tolerance of the input frequency range set to 50Hz ?

Hello,


I have a ESS with a Multiplus II 48/5000/70-50 230Vac inverter, the grid frequency is 50Hz.

In the manual I see 3 options for the input frequency range: : 50, 60 or 45 – 65 Hz.


My grid operator requires using of a Frequency Monitoring Relay (together with Voltage Monitoring Relay, Overcurrent Monitoring) that should disconnect the invertor from the grid in case the frequency becomes lower than 48Hz (for 10sec) or higher than 50.3Hz (for 1 sec)

I wonder what will be the behaviour of the Multiplus II if I set it to frequency 50Hz (the first option), what will be the frequency tolerance accepted by the inverter and at what deviation it will be disconnected from the grid? Also, what willl be the reaction time?

Can the Multiplus II be configured to replace the required external Frequency Monitoring Relay?



Multiplus-IIfrequency
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@bbo@abv.bg

Depends on the grid code used?

If no grid code, I have seen the inverters be comfortable 0.5 Hz up and down.

They do not like sudden changes and will disconnect then.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

bbo avatar image bbo commented ·

Hi Alexandra,

Thanks for the reply! Is there any specification on this behaviour?