ESS will not discharge battery

Hi brains trust,

I am having an issue where my battery will not go in to discharge in the ESS.

Victron MultiPlus II 48/5000/70.

Battery is showing all ok with no alarms in Victron and online

1702197940594.png


No alarms from the BMS

1702197973169.png

1702197990396.png


State of charge is 99%

1702198027632.png


ESS Settings all seem correct

1702198061054.png

1702198090376.png


Grid meter is reporting correctly

1702198120531.png

1702198145040.png


BMS is reporting that it is ready to discharge on both battery units connecting via RS232

1702198209186.png


I have run out of ideas on how to get this battery to discharge.

Battery units are 200AH 48v LiPoFe4 connected in Parallel via Lynx Distributor (400AH Total)

Anyone have any ideas as I am all out of them?

Thanks in advance!

Greg

ESSess discharging
1702197940594.png (50.2 KiB)
1702197973169.png (41.8 KiB)
1702197990396.png (40.2 KiB)
1702198027632.png (37.8 KiB)
1702198061054.png (51.8 KiB)
1702198090376.png (43.2 KiB)
1702198120531.png (45.1 KiB)
1702198145040.png (56.4 KiB)
1702198209186.png (7.5 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

15 Answers
netrange avatar image
netrange answered ·

Your Single Phase ESS must  be connected to the L1 from your ESS Meter !

Change the wiring ... then of will works .

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

glipschitz avatar image
glipschitz answered ·

Interesting @Netrange - thanks for that info.

I suspected that may have been the issue, however I thought it would also look at the total, rather than a specific phase.

I will try that out :)

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

glipschitz avatar image
glipschitz answered ·

Ok, that has been corrected now @Netrange but still won't discharge

1702200200460.png

Any other ideas?


1702200200460.png (45.2 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

glipschitz avatar image
glipschitz answered ·

Think I might just do a full power cycle on everything and start up the system from cold to see if that helps.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

netrange avatar image
netrange answered ·

Your Inverter-Mode is Inverting ? Is Power connected to the ACin or maybe a broken fuse ...

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

glipschitz avatar image glipschitz commented ·
AC-In connected to Load

AC-Out 1 connected to Fronius Inverter in AC Coupled mode

0 Likes 0 ·
netrange avatar image netrange glipschitz commented ·
Check your Multi for working ACin in the Remote Console ... Status LED in the Picture below is OFF.
0 Likes 0 ·
glipschitz avatar image glipschitz netrange commented ·

AC In All looks good.1702201667275.png

0 Likes 0 ·
1702201667275.png (12.4 KiB)
glipschitz avatar image glipschitz glipschitz commented ·

It's in BULK at the moment

1702201092232.png

0 Likes 0 ·
1702201092232.png (39.9 KiB)
glipschitz avatar image
glipschitz answered ·

There's a small cell imbalance which is coming down with the bulk absorption as expected.

Battery 1
1702201288153.png

Battery 2

1702201306049.png


1702201288153.png (6.3 KiB)
1702201306049.png (5.8 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ejrossouw avatar image
ejrossouw answered ·

What is your country code? If set to standard, it won't feed in.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

glipschitz avatar image glipschitz commented ·
I'm in Australia @ejrossouw

When you're referring to the country code, are you meaning for the grid?

It's currently set to Australia.


0 Likes 0 ·
ejrossouw avatar image ejrossouw glipschitz commented ·
@glipschitz Yes, that is the one. I thought the devices were no longer certified for grid parallel use there? Is the grid meter in front of ALL the house loads and what is its defined role?
0 Likes 0 ·
Show more comments
netrange avatar image
netrange answered ·

Check the "Parameter" from your Battery ... Maybe the DischargeCurrent ... DCL is Set to 0 ...

And a Warning Massage ?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

glipschitz avatar image glipschitz commented ·

That all looks good to me @Netrange

1702202764737.png

0 Likes 0 ·
1702202764737.png (34.1 KiB)
netrange avatar image
netrange answered ·

Try to force the System to Feed In! . ESS ... GridSetPoint to negative ... Look if that works...

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

glipschitz avatar image glipschitz commented ·

Nope, doesn't do anything. Tried that one earlier too.

1702203920619.png

0 Likes 0 ·
1702203920619.png (42.7 KiB)
netrange avatar image
netrange answered ·

Maybe a Configuration Problem with the Shelly for a 3-phase konfiguration with your 1-phase System and the ESS Setup for "all phases" ?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

glipschitz avatar image glipschitz commented ·
Perhaps, although I am only using 1 phase on the energy meter and have this at L1 reporting to Victron correctly.

If it wasn't reporting correctly to the GX, then it wouldn't be feeding the data to VRM either.

0 Likes 0 ·
netrange avatar image
netrange answered ·

And take a look into the workaround...

https://community.victronenergy.com/questions/125793/shelly-3em-smartmeter-with-venusos-cerbo-gx.html

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

glipschitz avatar image glipschitz commented ·

That is all based on Shelly EM3.

I am running Shelly Pro EM3. It's a completely different product.

I am running this code;

https://github.com/funkmaster86/dbus-shelly-pro-3em-smartmeter

0 Likes 0 ·
glipschitz avatar image
glipschitz answered ·

I'll order a Shelly EM (Single Phase Device) and see if that yields a better result.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

glipschitz avatar image
glipschitz answered ·

Perhaps @funkmaster86 can shed some light as to why the power meter isn't triggering the ESS as I am using his code from https://github.com/funkmaster86/dbus-shelly-pro-3em-smartmeter ? :)

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

glipschitz avatar image
glipschitz answered ·

Interestingly, the VRM ID of the Victron EV Charger has a fixed ID of 40.


1702243592903.png


It seems that a power meter code ALSO has a default VRM ID of 40 which is seems to be what everyones dbus-shelly code injects the value into. Only picked up on this when the EV charger integration with home assistant didn't work because of the conflicting ID.


Changing the ID in the config.ini to be 940 for the Shelly Pro 3EM does change it in VRM, but, the ESS still does not trigger. Did fix the EV charger integration though.

1702243702893.png


The mystery continues....


1702243592903.png (28.7 KiB)
1702243702893.png (25.7 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

glipschitz avatar image
glipschitz answered ·

Still no luck after replacing the power meter.

I have gone back to the beginning and factory reset the GX and reinstalled the ESS.

The new power meter is showing up and reporting the grid power as expected

1702341557893.png

The VRM Instance is set to 41 being unique in the system

1702341580723.png


Data is showing correctly on the dashboard

1702341622029.png

Data is displaying correctly in VRM

1702341706279.png


Any ideas? I'm stumped!


1702341557893.png (39.6 KiB)
1702341580723.png (39.3 KiB)
1702341622029.png (48.8 KiB)
1702341706279.png (151.8 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.