Multi Plus II - Stop the random Relay Test

We have a 3ph set up with MP2s with an ESS. We have the system working with a changeover switch, the system operates without issues bypassing the essential loads/charging the ESS and powering the loads from the Grid. We have only run the system powering the essential loads from the ESS for 10mins at a time, it operates as expected during those tests. The 1st incident after 7 days of faultless operation and second incident after 11 days of faultless operation, Relay Test Fault. The system appears to auto run a random relay test. It fails the test and switches off, Error 11. It appears that they were #45 0x8200024 (Error Occurred GND Relay Error) and #50 0x800002 Relay Test OK PE2 Closed Error (but states Relay Test Fault in Alarm Log) errors. These errors ocur out of office hours and no one is there to reset right away. When staff return and reset system it operates. Elec Eng is sure N and E are bonded correctly and seperate between essential and non-essential boards. Without this random test we would be fine. Can we stop this test from running?

Multiplus-IIerror
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

The test indicates a fault, and the system must respond to the fault condition.

It is not designed to test randomly though, it occurs when the relay is activated, either by a grid outage, programming setting or something else.

Disabling the test that occurs when the relay is changed is usually forbidden by the grid rules and standards compliance.

If you are certain the system is wired correctly, you will need to contact your dealer/regional Victron Manager to discuss what to do next.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stdl avatar image
stdl answered ·

Thanks Guy, understood, the test occurs due to:

1. Grid outage, does the test occur instantaeous to the outage, or when?, the inverters are servicing the load all the time (ready to UPS the essential loads) and yet the system does not fault mode, why is that if there is a wiring issue?

2. programming setting - please elaborate.

3. something else - have to smile at that, any chance of more guidance?


Thanks, Simon

13 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Hi @STDL

I've looked into the system briefly, and the first error #11 occurred on 2019-06-22 11:17:05.

As this is a 6 inverter system, please have an experienced installer check the system, and if he / she cannot find anything, contact your distributor for the next steps.

0 Likes 0 ·
Show more comments
nigelfxs avatar image
nigelfxs answered ·

Hi @STDL

I am not sure if this will help, but I have a Multiplus-II 3k unit (single phase) and the relay used to operate 2 or 3 times per day even though there was no noticeable dip in the mains voltage. This stopped when I updated the MP2 firmware from Version 453 to Version 459. The relay has been "quiet" for many weeks now :-)

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.