Hello everyone.I currently have 4 pairs of 2 x 410w panels connected in series to a 100/20 SCC each.The Voc of the 2 panels is 74 v and imp is 13,04. I'd like to put more panels on my roof,and I thought buying 8 550w panels.Can I connect a 550w panel with a 410w so my voltage rises?The 550w panel has 50 VOC and 13,11 imp and the 410w has 37 VOC and 13.04 imp.

Solar Panel
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

5 Answers
Kevin Windrem avatar image
Kevin Windrem answered ·

If you parallel panels with different voltages, the lower voltage panels will shut down. If there are no protection diodes, this could also damage the lower voltage panels.

For series connected panels, the lower current panel will dictate the current for the entire string.

If you are suggesting one 410 panel in series with one 550 watt panel, then yes that could work since the Imp is close. I'm assuming you have a 48 volt battery bank. Otherwise, you are limiting your output based on the 20 amp current and the battery voltage (960 watts for a 48 volt battery bank, 480 watts for a 24 volt battery bank).

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

conundrum avatar image
conundrum answered ·

Yes,the battery is 48v and the system works very well.I need more power and I thought buying bigger panels and use the same 100/20 mppt's.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

pierrot avatar image
pierrot answered ·
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1234enough avatar image
1234enough answered ·

Try this to see any potential loss's https://footprinthero.com/solar-panel-series-and-parallel-calculator

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

conundrum avatar image
conundrum answered ·

Thank you for the link,I managed to find an 540w panel with the same Imp value.Using the calculator I have 0 losses.This way I can increase my panels voltage within range and producing more power.