Hi Everyone,
I have 2 battery banks on site (15 battery per each) and I need to monitor them through BMV-712.
So I intened to use 2 BMVs for monitoring the both of banks, will this be working well?
P.S. The batteries are connected in parallel.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi Everyone,
I have 2 battery banks on site (15 battery per each) and I need to monitor them through BMV-712.
So I intened to use 2 BMVs for monitoring the both of banks, will this be working well?
P.S. The batteries are connected in parallel.
If you have 2 physically seperated battery banks, and only one at the time will be used, then 2 BMV's is ok. On the moments you would use both battery banks at the same time, you need to add up each BMV charge or load current value to get the total.
If you have both battery banks always connected in parallel, and if they are always connected and used at the same time, then 1 BMV would be better more easy.