VICTRON SMA

Helle all, I will have to instal a 120KWp with 120KWh batteries (BSLBatt lifepo4). I think about 9 x Multiplus II 48/15000 for distribution, 9 MPPT 250/100 foe each Multiplus and 3 x 25 SMA tripower on AC coupling. Would you have any feedback for compatibility with SMA ? Any example of similar installation ?

Thanks, all the best.

Thierry

victron community
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Michelle Konzack avatar image
Michelle Konzack answered ·

How do you do this:

I think about 9 x Multiplus II 48/15000 for distribution,

Only the models up to 5000VA models can run in parallel. If you wanto to build a 3-ohase system with 135kVA/108kW, then you have to use Quatros.


9 MPPT 250/100 foe each Multiplus

Maybe you should consider the RS 45/200 because with 9 smalk 100A MPPTs you can run into a balancing problem.


120KWh batteries (BSLBatt lifepo4)

I would say, your batteries are a little bit too small fot the Solarpanels (if you have 120kWp, you should have at least 360kWh of batteries, – 1:3 rule) and I am not sure, your LiFePO4 battries will be happy with a charging current of 2400A and nine 15000VA inverter can produce a cintinious load if 2800A and a peak load of 5600A, However, with this load, the voltage will sink in and the Ampers increase, hence you have to calculate with 3200-6400A.


I plan currently fir a customer an installation with 12 Quatro Inverter and have fight with the Power Rails, the placement of 8 battery sets if 200kWh each, the cable sizes and lenghts. Also the fuses needed (e.G. NH3)