question

kevintearocean avatar image
kevintearocean asked

Getting BMS system out of protection mode

I'm in a yard period and the marina lost power. The batteries were depleted so the BMS has gone into protection mode. Its my understanding that the batteries have the be charged to a point where the system is at a safe voltage level before the system comes out of protection mode.

At the present time if I flip the shore breaker on, the system powers up for approximately 1 minute, then all 4 of the Skyllas go into failure mode and the system shuts down.

However as the Skylla chargers are part of the system - I need to get the system running so the Skyllas will start charging the batts, so in a catch 22.

I'm hoping there is a system reset, but I can't find anything in any of the manuals or on any forum for a workaround.

Any advice greatly appreciated

Kevin

battery chargingBMSbattery protect
6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
@kevin.tear.

It would be helpful to know what battery so we can help with the BMS...

0 Likes 0 ·
kevintearocean avatar image kevintearocean Alexandra ♦ commented ·

Thanks @Alexandra - info on the system


Main service batteries

12 x Victron Energy Lithium-Ion 24V/180Ah


BMS:

2 x Lynx ION BMS 1000A


Chargers:

4 x Victron Energy Skylla-I 24V/100A


Any advice greatly appreciated


Kevin

0 Likes 0 ·