Hi.
Have just had a Multiplus 12/3000/50/ 240 volt inverter installed in our van.
Supplies power on output 1 both on and off grid.
No voltage on output 2, whether connected to the grid or not.
Is there a configuration issue
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi.
Have just had a Multiplus 12/3000/50/ 240 volt inverter installed in our van.
Supplies power on output 1 both on and off grid.
No voltage on output 2, whether connected to the grid or not.
Is there a configuration issue
With the default settings AC Out 2 becomes active with a delay of approximately 2 minutes after grid is connected.
-> see manual at 4.3.1
Just a suggestion for one possible cause.
check the unit using Ve Configure and a mk2 or mk3, to see if its had assistants installed or other settings changed in the past as these could be controlling the AC2 out.
maybe even upgrade the firmware to the latest version as this will also reset the Unit back to factory default as well.
Ok thanks, ill get the correct interface tomorrow.
Had a read of the information.
Maybe just settings.
Was this working when the installer commissioned the unit?
What is the source of the incoming 240-volt power? Has the incoming voltage been measured?
No it wasn’t working then.
Just followed the diagrams and connected as is.
I need to get the correct interface for the unit tomorrow
Maybe then we can see the settings.