question

sparx avatar image
sparx asked

Quattro Config Options for a 2 x 240V 180 degree apart Grid Connection

That’s 240V from L1 to N and from L2 to N, and 480V from L1 to L2.

I have no use for any voltage other than 240V.

For my use what’s the benefit in configuring 2 x quattros in “2 phase 180 degree” mode? Is anything different to just running 2 x stand alone separate single phase systems?

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@Sparx

Yes you can. And yes you can load each phase individually. With one correction.

Is your grid system supply 3 phases? If it is then 120° is the correct way to set up. Not 180°. The three phases are 120° apart.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

sparx avatar image sparx commented ·
Hi Alexandra,
It is definitely 2 phases and definitely 180 degrees apart.

Thanks.

0 Likes 0 ·
Show more comments