Multigrid 24/3000 back up system.

Hello,

A Victron Multigrid 24/3000 is used as a grid back up.
A 30mA differential relay is used at its output.
The relay trips with no obvious reason.

a) Whenever the unit switched from inverter back to mains on (i.e. when grid exists again)
After this tripping the relay is armed to operation and works normally but on (b) below.

b)for no reason and at irregular intervals. The relay if armed does not trip again but after some random hour.

multigrid
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Mark avatar image
Mark answered ·

I would recommend getting a qualified electrician/installer to check the setup and wiring.

It could be due to;

- A real earth leakage issue

- A faulty Residual Current Device

- The internal ground relay not being configured to close when mains power is disconnected

- No neutral to earth link on the mains side

- A neutral to earth link being present after the Residual Current Device

- Multiple neutral to earth links being active at any one time

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexis Kalogerakis avatar image
Alexis Kalogerakis answered ·

Dear Mr. @Mark,

we replace the Multigrid 24/3000/70-50 with 26xxxxx firmware with Multiplus 24/3000/70-50 with 26xxxxx firmware and we don't have any problem.