question

smartsana avatar image
smartsana asked

Problem with EasySolar-II GX Installation - Goes OFF when Grid is disconnected

We have recently started facing issues with an EasySolar-II GX installation which has been functioning well for the past 3 years. The system is configured to automatically switch to solar when the grid is not available.

The system goes off each time the grid is unavailable.

The batteries all seem healthy and are charging but there's a constant battery low alarm.

The GRID input is constantly abnormal, with values indicating negative input most of the time.

screenshot-2023-11-09-091616.png

Here's the console reading for the MultiPlus-II parameters

1699518101361.png

Alarm logs:

screenshot-2023-11-09-092654.png

I will gladly provide any more information to get assistance with this issue.

Thank you.

EasySolar All-in-One
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
@smartsana

What batteries do you have? Is there a fuse between have you checked it?

If anything it is likely the batteries or connection to them that is not well.


1 Like 1 ·
smartsana avatar image smartsana Alexandra ♦ commented ·
We have 12 Ultracell GEL batteries. Yes, there's a fuse and the connection is fine. What about the grid indicated power ? Is it normal ?


Thanks for your help.

0 Likes 0 ·
JohnC avatar image JohnC ♦ smartsana commented ·

@smartsana

No, it's not normal. The Multi is in Bulk state and 'Charging' to a low Battery V, but it isn't. Would be interesting to see the Vbat on the Multi screen, without that V that I suspect is being passed on by DVCC. Look for a disconnect (partial?) between the Multi and the batts.

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ JohnC ♦ commented ·

You could also have a couple of weak batteries in the pack.

Do you have balancers have you done bank rotation etc for maintaining the balance? And make sure all interlinks are tight.

0 Likes 0 ·
1 Answer
Dean Perry avatar image
Dean Perry answered ·

Is this set up as ESS or as a UPS? If you manually disconnect the grid, isolate the pv and run just from batteries, how quickly does the voltage drop on them?