I want to be off-grid on a new home. So, I'm planning to install a EasySolar-II 48/5000. The target is to have an acceptable production on very cloudy days (so, minimize battery capacity).
500W panels seems to fit "perfectly" for the 250V limit (JA Solar JAM66S30-500). The Voc of 45,6V makes an array of 5 produce 228V. My plan is to have 3 parallel arrays.
I would consider -10ºC, as temperature value for calculation at my location (42ºN). But almost never goes under -8.
That makes 249V at the worst case scenario. Cabling of each array will be 20 meters long (that adds some voltage drop).
Is it way too tight?
Can something bad happen if I open the circuit with some contactor (DC rated) if 249V is reached? (and then return after conditions are suited better).
Thanks