smartshunt to measure charging

Hi,

Im trying to connect some small wind generators with built in electronics that provides 48VDC to a multiplus II inverter with a 48V lead acid battery.

Im planning to use a smartshunt to measure the power from the wind generators, and the MPPT controller measure to the PV power, is it possible to run this setup and mange the battery charge/discarge and SoC or do i need one additional smartshunt on the battery?

victron.png


SmartShunt
victron.png (64.0 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Justin Cook avatar image
Justin Cook answered ·

As drawn, the SmartShunt in the system is a DC energy meter measuring your wind output. For battery SOC and usage information, you need another SmartShunt or a BMV-7xx in battery monitor mode, connected as the first and only thing connected to the battery bank negative.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

heds avatar image
heds answered ·

Ok, i will add one smartshunt for the battery.

Thank you for the quick reply Justin!