I have newly installed a system in my RV. I have 2 x Multiplus (24/5000/120-100) connected in parallel, a lynx distributor, SmartShunt 500A/50mV, 2 x MPPT 250/60 rev2 (v1.61) solar charge controllers for 1.6KW of solar panels and a 840Ah LiPO4 battery bank, this is monitored by a CerboGX (v3.10) and a digital multi control 200/200A GX.
I have checked the firmware on all devices is the latest version and have used VE configure to configure the 2 x Multiplus in parallel. Everything appears to be working well with the solar charging for the batteries and the Invertors are running well from the battery bank for AC loads. However when I switch on the shore power the Multiplus' recognise the shore power but trips the breaker after about 15 secs. I have checked the wiring and it all appears fine.
As a further check I have tried the system by making the master Multiplus a stand alone and then everything (invertor and charger) when switching on shore power is fine and there is no tripping. I have enabled the prioritise other energy sources in the advanced tab in VE configure so the charger switches to sustain mode as the batteries are currently at their sustain voltage so this is what I expected to see.
When I reconfigure the multiplus' back to a parallel system then it trips again. I have both the Master and the Slave configured with the same settings so wondering if this is where the issue lies.
Would appreciate someone pointing out my obvious mistake
Many thanks