In VRM AC Input to zero and also AC load?


Good evening and thanks to all of you,

after months of good weather the rains arrived and also a small problem, hopefully manageable.

Why I have more than 1Kw in AC input going to the loads and battery. While in the VRM it shows me 0 W Grid and also AC load 0 W?


My System is MultiplusII -GX only L1 phase and no ESS function.


Thanks to everyone who wants to point me to a solution.

Best Regards

Manuele


1697837601085.png


1697839241659.png

Multiplus-II
1697837601085.png (90.9 KiB)
1697839241659.png (65.8 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
manuele avatar image
manuele answered ·

Sorry, I'm answering myself, a terminal had slipped out of the SCT-013 energy meter. For this reason it no longer reported the measurement.

Good day to the whole Victron Team.

Manuele