3x us3000c - is one power cable enough?

I have 3x pylontech us3000c connected. Connection is done by one original pylontech cable. Question is if it's enough? Or how to connect next one cable? Thanks

Alex

Pylontech
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Alexandra avatar image
Alexandra answered ·

@Alda

What is is it running?

You can daisy chain the batteries (short cables come with each battery) and the cable is rated for 100A so is just a little short of a 5kva if running hard.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

alda avatar image
alda answered ·

actualy I have like this :

20231012-180818.jpg


so to be sure I must do it like this ? :

19872-batteries-to-busbar.png


means add next wires on the place where is cap now ?


15 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image kevgermany ♦♦ commented ·
No need, as long as your loads are within the cable rating.