question

theshenks avatar image
theshenks asked

Priority solar in ess connected to ac, ac2 question

Priority solar in ess but connected to ac what happens to ac2? does it still feed from the grid

ESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @Theshenks

Could you explain what your question is?
Also describe your system to get better answers.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kalito avatar image
kalito answered ·

Interesting and surprised this has not been answered yet. @Theshenks and @Daniël Boekel (Victron Energy Staff) my experience on AC2 out on Multi with ESS shows that in the presence of grid with self consumption setting with battery life AC2 behaves just like AC1. A disappointing discovery as the whole point of AC2 is loads you really dont want on backup/solar unless under special conditions (such as battery full amd PV to power these etc. )

You put your hot water heater on AC2 it works in bypass when system is backup. But alas implement ESS and your hot water heater runs on batteries at night if switched on unless you limit inverter output so that when you switch AC2 load excess above limit comes from grid.

7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Hi @Kalito

It wasn't answered because the question wasn't clear...

But as you describe it: yes AC2 out is the same output as AC1 but switched with a relay.

The history for this function is off-grid systems (boats, RV's, house without grid, etc). where some loads should only be powered if shorepower / generator input is available.

With the use of assistants, a lot of flexibility is possible for when AC2 is switched on/off, but technically it's the same output as AC1 and the system cannot measure what output is drawing what current.

The solution for you is to run the water heater in front of the inverter, not on the output.

0 Likes 0 ·
Show more comments
bulraydin avatar image bulraydin commented ·

Hello indeed I think your explanation seems quite correct. We have ESS installed and we have separated AC2 loads as the loads which should only work when mains is available. However in ESS, when the system is for example using mains and also the battery it seems to supply both AC1 and AC2. Then quite frequently the system disconnects AC2, although mains is still available... Is this a bug of ESS ?


I have the feeling under ESS batterylife, the system disconnects the AC2 whenever an overload situation happens, however this is not what I understood from AC2.


What is the solution to this problem ?

0 Likes 0 ·
Show more comments